General => Lounge => Topic started by: jcassity on September 12, 2008, 12:23:51 AM
Title: NEC Code question
Post by: jcassity on September 12, 2008, 12:23:51 AM
I sure hope someone here can help cause i cant find the answer in my NEC 2005 or the Ugly's or online or for that matter,, I just simply at random searching for any company willing to talk about my issue.
Pls site your answer with an NEC ref, there is a poorly served customer out there IMHO with several sites wired goofy.
We all know that circuit breakers, EEE Disconnects and fused disconnects must be cabled with the correct ampacity of wire size.
so, here is the question,,,,,,
Does this rule apply for  manual disconnects with spring loaded finger blades as well?
Its getting really bad with your local power company says " sir, your way over my head on that one" , same holds true with Telcordia but i await a call back from one of the editors of the NEC 2005 that works for Allegheney Power.
A little background,,, and this happens to be a DC Power Plant application.
I have noticed on about two dozen Time Warner sites and a few PacBell sites that the 1520AH battery string will have a 1200A manual two finger blade disconnect on the output (not a breaker, no fuses, no current limiting at all even in a thermal runaway situation).  However,, I only see one 350kcmil cable on the disconnect and one 350Kcmil cable on the return.  The ampacity of 350 at 75degC "in raceway is only 310A.
This battery cable travels a one way distance of 60' to the DC rectifier plant collector buss.
If i were to engineer that situation treating the disconnect as a breaker (which it is not),  the formula would be...
11.1 x Loop Lenght x 80% of max breaker size / .25 voltage drop.
so..... 11.1 x 120' x 960A / .25vd = 5,144,880cmil
This setup would require at worse case 3 cables of 750Kcmil per polairity or 6 total runs.
I have enjoyed my never ending frustration with the NEC and its glorious three or 4 paragraph reference to DC power only to cover such silly topics isolated to grounding.  Even in the Emergency power section of the nec, we get a smidge of tech speak with reguard to batteries.
As a side note,, I asked Allegheney power the following question as to help me reach my goal.
I said,,,,,,,,"If an employee of yours arrived at a site and was reading the meter of a 400A single phase service and while doing so, glanced over and noticed a manual spring loaded finger blade 600A disconnect, What would you think?"
My answer directly from two engineers was the following:
"the NEC strictly states the disconnect must not be rated less than the service rating".
Yep, they are right, i would be an idiot to disagree.
I asked if this site needs to match the disconnect to the service size an they said NO.  The customer has obviously planned on room for upsize service in the future.  Yep, Ill agree to that,,(although the only obvious growth would be 120/208 3phase).
I asked if its a violation, they said no.
So back to my original issue,,I have a 1520AH battery stack wired for -48vdc and the disconnect is 1200A but the cables are too  small IMHO, and ,,, to beat all,,, the customers dc power load currently is 400A.  For now, the site is not in trouble,, but as soon as they add more DC power telephony gear, the dc power draw will increase.  They do not even have a current limiting device in line with the hot leg of the battery stack.
Hope someone here and answer the above question,, ignore the rest of the rant.
All i need to know is what ref is there to rules on wiring non fused blade disconnect and if there is a ref to treaing them the same as breakers with respect to ampacity rating.
Post by: jcassity on September 14, 2008, 01:05:10 AM
these guys over here are getting me ready to go into thermal runaway.
I know i can be a dick but for crist sakes, these guys are the very reason my job is so darn difficult.  I thought this was going to be a good site to stick with but apparently not.
Imagine on most of our site here, when someone asks a question, they are answered with a question each and every time with little or no real substance to thier answers.
http://forums.mikeholt.com/showthread.php?t=104100